Dave-n-Marjorie 06-25-2013 12:07 AM

Basement SCS A/C Service at Newell.....issues and HELP NEEDED!!!!!!
 
Hi everyone. I am in need of some help and input, hopefully by tomorrow morning. I am sitting here spending the night in a bay at Newell and it is not going well. I have a double unit. Before arriving here I installed a new board, all capacitors new, new thermostat, new #2 compressor, cleaned unit top to bottom....leak tested, all coils and fins look new.

#1 compressor was not working as good as it should and at 16 years old, I knew it had to be replaced. Talked to Cressly and Dwight last week a few times and they told me what the ranges should be and I need to replace compressor #1 and "tweak" both. I decied to go out of my way and bring it to Newell, shipped a NEW compressor to Newell, made an appt with Tommy and drove here.

So today Dwight pulls unit out, replaces #1 compressor. By 3pm, unit is turned on, its supposedly 90 deg inside the covered service bay and its 80 in the rear bedroom of the coach. He turns it on high which uses both compressors. I asked him if I can just keep it on low to run compressor #1 only to test, as I know the second new compressor works. He said it wont cool at all with just one compressor on, it needs both but gave in and I turn on just the one compressor (not on high)

The air is blowing in the bedroom register 75deg. The air at return under stairs is 80deg. Thats a 5 degree difference!!!! He said thats because its 90 outside and on one compressor, THATS THE BEST IT WILL EVER GET.

He then turns on the second compressor and it drops to 69deg out of bedroom register. 11 degree difference.

My FRONT SINGLE unit has a 21 degree difference at same temps!!!! Dwight cant explain that one!!!!

This is NOT in direct sunlight in the covered shop garage!!! Not in the REAL HEAT!!!

Tommy says he should have booked me with Cressly next week (he is on vacation this week) and Dwight is only one here who knows these a/c's.

Dwight says NO Newell basement airs have ever worked well in high heat (90 deg), and only way to fix is to replace them with roof airs. He packed up his tools, sealed up unit and is done!!!!!

MY A/C's ARE WORKING WORSE THAN WHEN I GOT HERE!!!

I AM BEYOND DISSAPOINTED!!!

What do I do?? Dwight himself told me last week should be 18+ degree difference and now 11 degrees is acceptable???

Dwight said he will pull unit open again tomorrow, so he can test each unit seperatly. HE WANTS TO TEST AT 7AM WHEN ITS COOL OUT!!! Plus I am spending night in the bay...even cooler!!! The numbers will be skewed as it will be cool out!!

If you have any advice please call me tonite till midnight or first thing in the morning. three five two 223-9494.

Thanks in advance,
Dave

NewellCrazy 06-25-2013 12:43 AM

Dave & Marjorie I hope this thread helps.


"I have just had my basement SCS air fixed and the solution may be important to someone.

The dual compressor unit was giving us trouble recently, not blowing as cold as the single front unit and the fan wouldn't turn off. I called my house ac service company and persuaded them to service my coach. The tech traced the problem back to a faulty thermostat. I told him I would order one and call him back for the install."

Link to Thread : https://www.luxurycoachlifestyle.com/...-solution.html

NewellCrazy 06-25-2013 12:47 AM

I will also chime in with this.

The first step in troubleshooting a low cooling complaint on the basement AC is to check the amperage draw on the compressors. First turn off the AC and wait 5 minutes, then turn the AC on with the thermostat set at least 10 degrees below interior temperature. Watch the monitor to see how many amps the first compressor draws when it comes on, which is usually a minute or so after the fan starts. A few minutes later the second compressor will turn on which will be indicated by a change in fan speed. Watch the monitor on the other power leg (if the first compressor was on leg one the other one will be on leg two) for the amp draw on the second compressor.

If both compressors are drawing in the 13 to 16 amp range (depending on the heat load), and they are drawing the same amperage, the system is operating to spec. and no repairs are indicated, but if one compressor is drawing considerably less amperage, you have a refrigerant (R 22) leak that needs to be repaired, If one of the compressors draws no amperage, you have a control board problem or a bad compressor.

Dave-n-Marjorie 06-25-2013 01:15 AM

Hi Sean, Thanks for responding. Fans work perfect and go on high when second compressor kicks in. Dwight says amps are within spec range and in his words "perfect" 14 and 16 taped up on high. He pressure tested both sides with Nitrogen gas and zero leaks. Vaccumed down for over an hour before r22 added. Both brand new compressors have proper amps and took r22 as a new one should, and a brand new control board along with all start capacitors.

Todays bill topped $1,000 here at Newell with a 5 degree difference from discharge vent to return. Is worse than when I brought it here. That is not acceptable in my book. These guys are getting $110 an hour, they are supposed to be the best. I have replaced every single component and they cant get it right, and my front single unit right now is kicking out 20 degree difference.

I have over $3,000 invested in this unit almost every part is new, and still not cold. About to give up!!!

NewellCrazy 06-25-2013 01:23 AM

I agree 100 percent with you. Did you read through that whole topic I gave the link to?

Dave-n-Marjorie 06-25-2013 01:26 AM

Yes, it really didnt help since all parts on this double unit are brand new and work perfect. Just doesnt cool within spec. Then it then went off on a inverter charger topic.

Quote:

Originally Posted by NewellCrazy (Post 35708)
I agree 100 percent with you. Did you read through that whole topic I gave the link to?


Dave-n-Marjorie 06-25-2013 01:31 AM

I guess my biggest issue is that I expected alot more from Newell than this. I can assure you if this is not fixed tomorrow within spec (18 deg difference) I will never be back! $3,000 for non working a/c is not acceptable....

86loco 06-25-2013 01:32 AM

Sorry to here about this Dave. We had stopped by the factory some 3 yrs ago with a good friend for service and honestly they have never returned. We don't even order parts from them as they do not have much for our year coach. A lot of folks really love the service experience though. I believe unless you have the bigger dollars to spend every time which is not in our case. My brother whom works for another union shop just chuckled when we shared our experience. He said he loves the perks hes gets from his job but thats union business.

Oh I have to believe their 24/7 service by phone must be much better than that of your in shop experience.

Neweller 06-25-2013 01:52 AM

Dave, what thermostat do you have? Has the stat been checked? Kind of sounds like the heat is coming on at the same time but if it's SCS it's air only. Heck, one time I had a similar problem at an office of mine and it was the darn wiring on the thermostat.

Neweller 06-25-2013 02:15 AM

Maybe I should add, that after I had two so-called professionals come replace everything, then had a friends uncle drive from LA to Las Vegas to fix the original problem in less than 20 minutes. Of course about $700 later. All for a simple problem. Kind of reminds me of my younger days replacing, starter, battery, alternator etc. to find out I had a bad ground. Darn it anyway.

Yachts 06-25-2013 02:21 AM

Guys I will tell you this.. I've only had my coaches to Newell 3 times.. Twice with Ron skeens 96 and once with my 99.. I had air probs with my 96.. And while I don't know the technical issues they were able to fix them.. When you check out whom ever is your service writer will go though stuff with you.. Even go ask before then and see if they can help..

I can tell you 2 tricks we did with my 96 to help cool the coach before we got everything working and I'm not sure why it works but it helped.. Your airs dissipate the hot air underneath the coach correct? Put a fan blowing air underneath where the hot air comes out.. It made a significant difference especially if we were on concrete.. Also I know it's not the best answer but it did help

Dave-n-Marjorie 06-25-2013 03:48 AM

New 12v Coleman Mack Thermostat with hi/lo fan and auto cool installed here at Newell last year. Only heat I have is aqua hot. Dwight checked thermostat at both ends and works perfect.

Pulled out my RVAC Service Manual. Specs are crystal clear. 95 deg outside air / return air 70 deg / discharge air 55 deg. 14 amps. Mine is 84 deg outside air / return air 70 deg / discharge air 67 deg. That is 12 degrees off from spec, not counting its 11 degrees cooler than spec test. I feel this issue is with the freon charging. They just dont know what they are doing or how to get it right.

I will talk again tomorrow morning to Tommy my service advisor, then probably to the shop manager. There is no reason why this A/C should not work within the specs. I have them in black and white, all parts on a/c are brand new. They have no excuses. I will not pay $110 an hour for someone to "experiment" vaccuming it down and putting freon back in. Thats why I drove all the way here. For professionals to fix it right the first time. I will make sure to fill every one in about my experience. These a/c's were installed from 94-04 and I am sure there are many out there.

Thanks everyone for quick response and phone calls.

I would love to hear from other owners whos SCS basement a/c's work well. Newell tells me they do not exist.

folivier 06-25-2013 04:02 AM

How about a totally different direction? Get out your IR temperature gun and check all of your ducting to make sure there are no leaks into your basement bays. May be a longshot but if there is a leak then not all of the cooled air is getting into the coach.Good luck.

ccjohnson 06-25-2013 08:05 AM

For what it's worth, our '92 has original basement a/c's. 3 units, inside of coach with levelor's & drapes closed was 85 degrees outside in Phx with afternoon sun on drivers side of coach temp was 118 degrees. 85 was inside temp not discharge air temp. Dwight & Robert were techs that serviced our a/c's at Newell.

Dave-n-Marjorie 06-25-2013 12:55 PM

Latest this morning is that Newell is saying the RVAC SCS specs are wrong and never worked even when new within specs. I find this very hard to believe! Can you imagine paying $800k for a 2000 Newell and the a/c only blows 6 degrees cooler than return???? They said no one has cool 16+ degree difference, and that its impossible. I find that hard to believe......

My front single unit has a 21 degree difference!!!! I drove all the way here, with promises that if I replace every part brand new, it would run within specs. We are at 1/3 of specs and I am paying $110 an hour for them to "experiment" for two days. No leaks as we are taking air temp at unit discharge, not inside air vent.

ccjohnson 06-25-2013 01:22 PM

Any chance there is internal debris in the evaporator coils?

GringoPhil 06-25-2013 03:08 PM

I say if Newell can't fix your issue your service should be free!

NewellCrazy 06-25-2013 05:09 PM

Quote:

Originally Posted by Dave-n-Marjorie (Post 35725)
Latest this morning is that Newell is saying the RVAC SCS specs are wrong and never worked even when new within specs. I find this very hard to believe! Can you imagine paying $800k for a 2000 Newell and the a/c only blows 6 degrees cooler than return???? They said no one has cool 16+ degree difference, and that its impossible. I find that hard to believe......

My front single unit has a 21 degree difference!!!! I drove all the way here, with promises that if I replace every part brand new, it would run within specs. We are at 1/3 of specs and I am paying $110 an hour for them to "experiment" for two days. No leaks as we are taking air temp at unit discharge, not inside air vent.

Anymore News?

Neweller 06-25-2013 07:33 PM

It's either DIY or DAP. It's an owners personal preference and choice.:bandit:

Neweller 06-25-2013 09:56 PM

Dave is awful quite all of a sudden, hopefully he didn't collapse from heat exhaustion. I feel more for Marjorie having to deal with the ruckus in all this. Dave, you didn't head down to Foretravel by chance did you?